I need a UPS.

I know how to fit one but i'm not sure of the type/size/battery type.

It does not need to be continuous as its running an electric gate and I do not want people from getting locked in.

The gate draws 16 Amp single phase but i'm not sure of its start up load at this time (Its not been fitted yet)

The power does not go out for long if ever but might need to open the gate about twenty times before the power goes back on.

The gate is 130 meters away from the supply but due to the volt drop I could fit it in a local feeder pillar.

Any ideas?

 

Link to comment
Share on other sites

Is it really 4kW? That sounds like a pretty hefty motor. That could be the inrush current rating?

anyhoo, find out the kVA required and get an UPS that can supply that much power. Duration of supply is then determind by capacity but I think you'll be looking for a decent bit of kit.

Link to comment
Share on other sites

4 minutes ago, corsechris said:

Is it really 4kW? That sounds like a pretty hefty motor. That could be the inrush current rating?

anyhoo, find out the kVA required and get an UPS that can supply that much power. Duration of supply is then determind by capacity but I think you'll be looking for a decent bit of kit.

Its a eight foot high sliding vehicle gate to keep people out.:)

The gate manufacturer has specified a 16 Amp supply so I'm hoping it includes full start up load.

Link to comment
Share on other sites

Youre going to need a shed load of batteries and that motor I would suspect would be a high torque motor , so will use a lot of battery capacity ............. 

Link to comment
Share on other sites

Don't they normally have a manual override so you can open/close in event of power failure, like opening a sluice gate on a lock?

Link to comment
Share on other sites

@finkangel I think you're looking more for a standby generator than UPS.

  • Like 1
Link to comment
Share on other sites

1 minute ago, IanK said:

@finkangel I think you're looking more for a standby generator than UPS.

You could be right. Not that hard to do either. 

Link to comment
Share on other sites

As said about the generators, when I used to look run up generators for banks, we used to drop the incommer supply to allow the ups to hold the servers , while the generator kicked up to speed and within 30 secs , the generator was on line and supporting power until mains was put back on. I dont think we had more than 5 mins ups support before we were in problems . 

  • Like 1
Link to comment
Share on other sites

The trouble with most solutions is unless you are rigourous about maintenance, they will do a Fawlty Towers fire extinguisher job on you every time you need them, so don't forget to allow for that aspect. A battery based UPS is fine in the right scenario, as is a backup supply. You don't appear to need sustained power, just a backup, so I think I'd probably favour a generator as well TBH. At my last place we had a range of solutions for various systems. Most critical had dual battery UPS fed from A supply that had flywheel UPS to hold up supply while the generators fired up and stabilised (two redundant systems of same), less critical had battery UPS on a different single generator backed supply. All systems got checked on a regualr and routine basis, fuel reserves were montired to ensure they didn't degrade, replaced as required. It can get expensive.

  • Like 2
Link to comment
Share on other sites

  • 1 month later...

@finkangel if you're not sorted. I install auto gates . Let me have details or a picture of the motor. I am unaware of any single phase motor that draws that much current 

Link to comment
Share on other sites

1 hour ago, neptune said:

@finkangel if you're not sorted. I install auto gates . Let me have details or a picture of the motor. I am unaware of any single phase motor that draws that much current 

Thanks. 

The gates will be going in next week so I'll have a look. 

 

Link to comment
Share on other sites

Sounds like a manual override would be the easiest solution here. I'd check with the supplier to see if there is an override function. 

Link to comment
Share on other sites

45 minutes ago, Deanspoors said:

Sounds like a manual override would be the easiest solution here. I'd check with the supplier to see if there is an override function. 

This is looking Like the easiest approach. 

Link to comment
Share on other sites

Is this for 'Fort Finkangel'?

sorry i had to ask ???

  • Like 1
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...

Important Information

Please review our Terms of Use, Guidelines and Privacy Policy. We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.